I know this question has probably came up at least eleventeen hundred times.
I am reviewing a set of drawings for an RV/Boat storage facility which is going to built using "pole barn" type construction and will have metal siding installed.
The engineer has a note on the drawings that states "Building metal veneer to be grounded per NEC 250.116 (fpn). Use copper clad steel rod 3/4" diameter and 10'-0" long spaced at 100'-0" maximum - use #1/0 copper wire."
I know that if this method is used that all these ground rods will have to be bonded back to the grounding electrode system for the service....... the question I have is what is the proper method to bond this veneer? Will a separate connection need to be made to each panel due to the panels only overlapping and fastened with screws or nails? What about all the corner mouldings, etc.......?
Pete
I am reviewing a set of drawings for an RV/Boat storage facility which is going to built using "pole barn" type construction and will have metal siding installed.
The engineer has a note on the drawings that states "Building metal veneer to be grounded per NEC 250.116 (fpn). Use copper clad steel rod 3/4" diameter and 10'-0" long spaced at 100'-0" maximum - use #1/0 copper wire."
I know that if this method is used that all these ground rods will have to be bonded back to the grounding electrode system for the service....... the question I have is what is the proper method to bond this veneer? Will a separate connection need to be made to each panel due to the panels only overlapping and fastened with screws or nails? What about all the corner mouldings, etc.......?