Code requires bonding of metal water piping systems. A PEX water piping system is not a metal water piping system even if it has metal fittings... and I've not seen nor heard of any fitting being over 18".What has to be bonded in a pex water piping system, residential? Someone mentioned fittings greater than 18 inches but I'm hoping to find a code article to confirm it.
Pex doesnt have to be bonded. Qest, otoh, should be bonded to a large, metal, earthed object, like the bottom of a 40yrd dumpster.
Ha ha!Pex doesnt have to be bonded. Qest, otoh, should be bonded to a large, metal, earthed object, like the bottom of a 40yrd dumpster.
IMO, if you have a metal piping system throughout the remainder of house, Yes. I would guess that all you have left are bits and pieces left in the walls and to me, that is not a piping system.Here is an interesting situation that has come up in abandoned homes the basement copper water pipes are often cut and stolen. The new owner replaces them with pex. Are you required to bond around the pex pipiing to ground the metal pipng system that runs through the house?
Qest?
IMO, if you have a metal piping system throughout the remainder of house, Yes. I would guess that all you have left are bits and pieces left in the walls and to me, that is not a piping system.
Qest?
I didn't know so I looked it up. It's polybutylene plumbing.I don't know what it is either. Given the context I guess that makes us lucky.
Source: http://www.polybutylene.com/poly.htmlPolybutylene is a form of plastic resin that was used extensively in the manufacture of water supply piping from 1978 until 1995. ...
Qest (or Qwest, Quest) pipe was what the plumbing industry used for 15 or so years, to out-do our AL wire and ca 1975-1980 FPE panel debacles. The only difference is that no matter how you install that piping, it fails. There's probably not much of it left seeing that it's been 20+ years since it was installed and has a life expectancy roughly half that.
Just bond all of it with a minimum of 30 lb. monofilament, the picture below is in violation since it used a copper wire.What has to be bonded in a pex water piping system, residential? Someone mentioned fittings greater than 18 inches but I'm hoping to find a code article to confirm it.
Just bond all of it with a minimum of 30 lb. monofilament, the picture below is in violation since it used a copper wire.
Roger
We need to take a step back, why are metallic water piping systems required to be bonded?
In case its energized and to clear a fault.
What would energize the isolated metal stub outs under a sink?
In Washington we have a state rule that addresses bonding non metallic piping systems, the metal stub outs are not required to be bonded