Re: Bonding of PEX water piping
As for the waterpipe of enterance into the dwelling is really 99 % of the time in dwelling units the meter is outside the dwelling so the main reason we BOND is required in 250 as part fo the GES as listed in 250-50 ( the 5 and 10 rule applies on this ) but basically I guess what the AHJ in our area is saying is that it is serving as the GES...and nothing more when it comes to past the PEX point.
[ January 09, 2005, 11:24 AM: Message edited by: radiopet ]
How about 680-73 I think would cover this...hmmm....now I would think since these units have to be on GFCI when you bond all metal parts of the system together it would take care of this ruling and would not require a tie back to the water supply system if non-metalic like PEX.Originally posted by pierre:
On the load side of the cold water meter (if the meter is located inside the building), you are not grounding, but bonding the water piping system. As in this thread, the water piping system is plastic and would not require bonding as per 250.104.
As Bob has mentioned, there is no real need to bond to the cold and hot water stub pipes from a basin (if the water piping "system" is plastic), how likely is it they will become energized?
Would you require the water stubs (if metallic) from a jacuzzi (hydromassage tub) to be bonded, even if the water piping system is plastic?
Pierre
As for the waterpipe of enterance into the dwelling is really 99 % of the time in dwelling units the meter is outside the dwelling so the main reason we BOND is required in 250 as part fo the GES as listed in 250-50 ( the 5 and 10 rule applies on this ) but basically I guess what the AHJ in our area is saying is that it is serving as the GES...and nothing more when it comes to past the PEX point.
[ January 09, 2005, 11:24 AM: Message edited by: radiopet ]