Bonding of Rigid steel metal conduit.

Status
Not open for further replies.

josh4u24

Member
Location
Dammam
We have a burried cable coming above ground through a rigid steel metal conduit.The cable will be terminated in a push button in an existing switch rack. Do we need to bond the rigid steel metal conduit at both sides to grounding.
 
We have a burried cable coming above ground through a rigid steel metal conduit.The cable will be terminated in a push button in an existing switch rack. Do we need to bond the rigid steel metal conduit at both sides to grounding.

Just use bonding bushings.
$_35.JPG


Welcome to the forum......:)
 
Will the RMC terminate in a grounded enclosure? If so it's possible that nothing further would be required.


Welcome to the Forum. :)
 
Will the RMC terminate in a grounded enclosure? If so it's possible that nothing further would be required.


Welcome to the Forum. :)
More precisely, will the RMC terminate to a grounded enclosure? The difference is significant in that many stub ups terminate in an open-bottom enclosure without actually terminating to the enclosure. Those type of stub ups need bonding.

@josh4u24... welcome :thumbsup:
 