Bonding Pull Box ahead of Service Disconnect 250.92

Status
Not open for further replies.

xguard

Senior Member
Location
Baton Rouge, LA
I have a pull box ahead of a service disconnect. There are no splices in the pull box. The box is connected to the disconnect with RMC. In order to bond the box to the Grounded Service Conductor, is it permitted to run a conductor (sized based on 250.66) from the Neutral Bus in the Service Disconnect back to the pull box and attach it with a lug?
 

iwire

Moderator
Staff member
Location
Massachusetts
I can't think of anything prohibiting that.

But why not just tap the grounded conductor as it goes through with a split bolt or other type of tap device?
 