Do I need to install the green bonding screw in a 50 amp, 240 GFCI breaker box for a spa located outside?

Thanks to all who reply!
 

iMuse97

Senior Member
Location
Chicagoland
No. keep neutral and ground paths separate all the way to the main panel where they must be bonded together, but no other place.
 

barbeer

Senior Member
I personally do not see how we can effectively answer your question, we do not have all the facts needed.
For starters: is there a neutral conductor at the disco
I would hope there is a grounding conductor.
which of these is attached to the bar you are asking about.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Do I need to install the green bonding screw in a 50 amp, 240 GFCI breaker box for a spa located outside?
It depends, as you see, on whether there is a neutral and a place to land it. A real spa disconnect will contain both an isolated neutral bus and a bonded EGC bus.

An A/C disconnect won't have a neutral bus. The enclosure should always be bonded to the EGC, and a separate neutral should never be bonded to the enclosure.
 