when protecting the gec using emt does the emt have to be connected by bonding back to the conductor? if so why?
stew said:when protecting the gec using emt does the emt have to be connected by bonding back to the conductor? if so why?
wbalsam1 said:Would non-ferrous EMT also have to be bonded? Doesn't seem like it? :-? :smile:
iwire said:No
Non-ferrous EMT?
Do you have any?![]()
Now I might run PVC and if they did not specify ferrous raceways I would have to bond my PVC...:grin:
wbalsam1 said:Would non-ferrous EMT also have to be bonded? Doesn't seem like it? :-? :smile:
roger said:That be refering to Eluminum Metalic Tubing? :wink: :grin:
Roger
roger said:That be refering to Eluminum Metalic Tubing? :wink: :grin:
Roger
stickboy1375 said:Art. 250.64 (E) I think you bond the raceway to ensure the raceway and conductor are in parallel with each other...
![]()
infinity said:In looking at this illustration, would a bonding locknut within the panel satisfy the NEC?
stickboy1375 said:Code says both ends need to be bonded to the GEC...
iwire said:Yes it does, but it does not specify how that must be done.
At the panel end the conduit is bonded to the GEC by way of the panel steel.