Why do the primary conductors look larger than the secondary’s? VD compensation or my eyesHere's a different size XFMR but the concept is the same. In general MIBG's are not required (except for on the GEC) but guys seem to always use them anyway. There should be a ground terminal for all of the connections.
What you should have is connection wise is this with the corresponding table:
Primary EGC-T250.122
Secondary SSBJ-T250.102(C)(1)
SBJ-T250.102(C)(1)
GEC-T250.66
Neither VD or your eyes unless you consider that they didn't see that the secondary has two sets of parallel conductors.Why do the primary conductors look larger than the secondary’s? VD compensation or my eyes
What are you using MIGB to stand for? Type in in to Google and it stands for Malleable insulated ground bushing. I am guessing for you it is some kind of ground bar.GOOD MORNING! I NEED SOME ASSISTANCE. I WANT TO MAKE SURE THAT I AM CONNECTING, GROUNDING, & BONDING THE MIGBs CORRECTLY TO A 225 KVA XFMR. MAYBE A PHOTO IF IT WOULD BE TOO MUCH TO TYPE. THANKS
Sent from my SM-G991U1 using Tapatalk
Infinity, why would you run your line side EGC to the XO point on the transformer instead of the case of the transformer (IE the ground bar)? IMO that seems like a code violation to me. I get that the electrons will find there way, but they depend on a bolt at the XO bar.Here's a different size XFMR but the concept is the same. In general MIBG's are not required (except for on the GEC) but guys seem to always use them anyway. There should be a ground terminal for all of the connections.
SBJ-T250.102(C)(1)
GEC-T250.66
Hope I'm looking at correctlyInfinity, why would you run your line side EGC to the XO point on the transformer instead of the case of the transformer (IE the ground bar)? IMO that seems like a code violation to me. I get that the electrons will find there way, but they depend on a bolt at the XO bar.
It's not, that's the GEC in a separate raceway (hence the bonding bushing) as Tulsa mentioned.Infinity, why would you run your line side EGC to the XO point on the transformer instead of the case of the transformer (IE the ground bar)? IMO that seems like a code violation to me. I get that the electrons will find there way, but they depend on a bolt at the XO bar
Woo. I’ll count it a blessing those weren’t snakes!!!Neither VD or your eyes unless you consider that they didn't see that the secondary has two sets of parallel conductors.![]()