M. D. said:I read it the same way as Dennis ,.. there is nothing wrong with bonding the EGC at the sub panel to water pipe electrode ,.. the interior gas pipe the,..metal hot air ducts ,..the air lines,. the building steel ,..the metal waste pipes ,..bond it all baby the more the better
Not only will it not interfere it will provide a lower overall impedance under fault conditions ,...assuming a complete metal piping system In this case two paths are better than one.
As stated earlier, the Gec is NOT for fault conditions to open the ocpd. Only the egc is. GEC utimately is to get the ligthing to earth via the ge. Why would one want to intentionally have a parrallel path of fault current on the any portion of the water pipe?? Read the definition of the gec and and tells you its connected to the service. It tells you also what the egc is for.