brother said:I see nothing in 250.104(A)(1) that prohibits additional water pipe bonding. The rule only specifies the required bonding and does not prohibit additional bonding once the required bonding is installed. In fact I will say that this additional bonding is directly permitted by 250.54.acrwc10 said:How do you justify, or interpet article 250.104(A)(1)?? The only time u allowed to bond the metal piping at another panel(sub panel) is a building with multiple occupancy and multiple buildings or structures etc..
So as far as physics/ mehcanically maybe there is no difference (i think there is) , but its definitely a code violation.
On second though, 250.54 does not apply as the water pipe is not a grounding electrode at this point in the system.