bonding Teck armor
ianis
the transformers I have installed all passed inspection. On most instalation we use Teck Cable as a feed from the splice box connected to the main disconnect. On the Teck we strip the outer jacket so that the dry connector grips the aluminum sheeting. I would say the alluminum sheeting on the Teck Cable is bonded and protected by the dry connector connected to the transformer casing. The cable also has a ground wire inside. Does anyone use ground bushing on the dry conector that brings the Teck Cable in the transformer?
Teck Cable
Teck Cable
I am in Canada. Teck Cable has a outer ruber membrane then a aluminium sheeting then another ruber membrane (if it for wet locations) then a sheet of paper and the 3-4 cables and the ground.
I've installed miles of TEK cable in power plants. The stuff we use is basically explosion proof MC cable. It looks alot like regular MC cable, but it has paper or plastic twine fillers packed tightly in the space between the wires, and a plastic/rubber outer jacket. When used with proper connectors it's listed for class1/div1 locations.
I've seen it with up to 35 #14's, 3/750MCM (about 4" OD, VERY hard to bend), and 3/500MCM 35KV (about 5 1/2" OD and doesn't really bend at all!). Always with a ground wire inside. The 3 wire types have 3 grounds.
To terminate it, you strip the outer jacket, then cut the armor off about 1" to 3" longer depending on the size. The connector has compressible spring inside that clamps around the armor, and a rubber sleeve (alot like a cord grip) that seals around the outer jacket. I've never used a bushing of any sort with it, by its nature it's pretty hard to get the wires to touch the inside throat of the connector.
When used with connectors designated and UL listed for TECK Cable, the connector and its connection to the body that it connects to is tested for SC carying capability and listed and approved for that purpose.
TECK cable is a CSA term and it is NOT recognized nor approved for Class I, Division 1 location as per the NEC.