Bonding / Termination for Class 2 HVAC control wiring

Eddie9v

New User
Location
Manitoba
Occupation
Red Seal Electrician
I am doing an install for 24vac HVAC controls in a northern territory. Class 2 100va. Inspector requested pipe sleeves in wall to protect free air wire, we did this and now he is requesting we bond each one. I bonded each with 14awg to the nearest electrical box but now they are asking for them all to be daisy chained with 10awg bond and then connected to a nearby electrical JB. I also am wiring valves and actuators, typically we install 1110 on duct and do joints in here but I am afraid the inspector is going to make us bond these boxes with 10awg as well... Is there any section of the code that makes me exempt from this. Never had this problem at home. Thanks!
 