stupid said:
If I bond the neutral and ground in the meter socket (Not a CT meter Socket). Do I bond the ground and neutral in the main disconnect or panel also. Addtionally, is a #6 CU or #4 AL largest I ever need to the ground rod even if there is no building steel or cold water pipe available or do I have to size the ground per Table 250.66
To your first question, I would first ask: what do mean by
"ground" ?
The ground from your ground rod to the meterbase is an
electrode grounding conductor.
If your electrode grounding conductor is connected to your meterbase, then the grounds that you're bonding to the main disconnect housing and main neutral are
equipment grounding conductors. Since they are different, it wouldn't be a parallel path.
But even if you were installing an actual parallel neutral and ground, it's not a violation when you're on the line side of the main disconnect.
ramdiesel3500 said:
So bonding the meter base to the GEC and/or having it bonded through raceways to the service panel should not constitute a parallel path unless the grounded and grounding conductors are bonded together twice.
Am I missing something here?
A parallel neutral and ground on the line side of the main disconnect may be unavoidable.
e57 said:
Just about every meter I install has the neutral buss on the can, no isolation bond by defacto. RMC required between meter and main. Main neutral needs to be bonded by code as well.
The neutral buss/bar is bonded to the meterbase housing. The neutral bar is bonded to the main disconnect housing. If there is metal conduit between the meterbase and main disconnect, the conduit is bonded to both meterbase and main disconnect housings. You have paralleled neutral and ground and that?s OK.
If I was inspecting your job, one thing that would ask you not to do is connect the electrode conductor to both meterbase and main disconnect. Pick one and stick with it. Metal conduit paralleled with the neutral from meter to main isn?t a problem, but a #6 electrode conductor paralleled with a large gauge aluminum neutral is bad news.
The Handbook picture on page #193 [Exhibit 250.8] shows you your options. The commentary after 250.24(A)(1) does a little more explaining. It?s your choice where to connect the electrode conductor.
David