Bonding to xo when not in use

Status
Not open for further replies.

sandsnow

Senior Member
Here's the label from the correct XFMR for the application

fpelabelresize.jpg
 

donkittyg

New member
x0 to ground

x0 to ground

I assume that your transformer is connected delta on the H1-H2-H3 windings and wye connected on the x1-x2-x3 windings. By definition the primary of the transformer is the source of supply side. In this case you have formed what is called a "Grounding Bank" by tying down the x0 or the wye tie you allow the currents of the 208/120V system to flow into the X0 bushing and be distributed by the delta windings on the high side.

Always float the X0 bushing in this cast. A wye-delta connection should be avoided in this case.

Don
 