Thanks for the reply Mike.
I tried bonding the 0 volt side of the terminal of the transformer to the chassis ground and it kept tripping the breaker for the transformer upon start-up. What is the cause of this? The transformer does have a separate ground terminal going to the chassis and it's ground is bonded to the 0 volt of the transformer.

This transformer is a step down transformer and has a 208V AC supply and has a 15amp circuit breaker over current.

Should I change the over current breaker to a time delay fuse with the same rating??
 

ActionDave

Chief Moderator
Staff member
Location
Durango, CO, 10 h 20 min from the winged horses.
Occupation
Licensed Electrician
I am closing this thread, in accordance with the Forum’s rules.

This site is designed for:

Contractors
Electricians
Engineers
Inspectors
Instructors
Other electrically related individuals
This NEC Forum is for those in the electrical and related industries.

Forum rules prohibit us from assisting a person to perform or assist others to do electrical work who are not qualified. The reason is that the forum’s owner does not want a person to get an answer to the question they asked, but not get answers to the other questions they should have asked and were unaware they needed to ask. Mike Holt Enterprises and the Moderators of this Forum do not wish to place you in danger, by allowing others to give you too little information to ensure that the installation is safe.
 
Status
Not open for further replies.
Top