The reason is a s?ngle phase system from high resistance grounded three phase system should not be used. I think there is a code prohibition for that.
You can tape single phase loads from a 3 phase high resistance, however when it comes to medical application isolated power the NEC states it must be totally ungrounded except for the line isolation monitor.
There are many forms of IT.
As has been mentioned medical applications (BS7671 has a whole new section to cover that).
In my case I?ve been involved with them on 11 and 3.3KV distribution where NER?s are used to limit earth fault currents.
Induction furnaces, the conductors and coils are water cooled so to provide a solid earth would be disastrous.
Mines and quarries, again to limit earth fault currents. (BS7671 doesn?t have a section for that).
But they aren?t used for general distribution. Which I believe is what the OP was asking about.
Not all inclusively. Most of the world doesn't use IT, but there are a few areas of the world where it is/was exclusive for domestic supplies.