Re: Bonding Water Pipe
As unfortunate as it sounds it's surprizing to see something that's basicly a matter of business being done in as little as three years in this state. You could lay odds on whether or not it's adopted on time.
Most people here put it on the water heater input pipe
I'm sorry I'm referencing 2002. 250.50 says you must include water pipe in electrode system if available. 250.52(A)(1) says it cannot be bonded more than five feet from enterance. I haven't seen a lot of water heaters within five feet of enterance.
250.104(A)(1) Seems to repeat 250.52(A)(1) without the 5' requirement. But adds the accessability requirement that's not in 250.52(A)(1). If I'm reading this right I think these two codes need to be combined into one code to releive the obvious difficulty that can be caused.
if the water comes in near the service the clamp goes on the pipe in the wall with a 2gang ring for access
I don't do get to do much new construction or similar situations where this would apply but that's a great method, I love it.
250.52(B) Electrodes not permitted.
250.52(B)(1)Metal underground gas piping system.
I'm not clear how I should interpret this but I'm told you bond the gas after the meter. Is the meter listed as an insulator or something? Cause if not I think that violates 250.52(B)(1)
I personally hate the idea of bonding the gas pipe. If you want to make an ignition spark that gets you half way there. (Hi Charlie).
Most people here run continuous from panel to ufer below then to CW then to gas. It's been done that way for so long, the residential inspectors won't accept anything else, then that's where I get involved to let them know another way is possible.
I'm on board with you here Larry. I'm running into severe resistance on this. But I will not accept being compelled to do things based on ignorance. I keep hearing how it's not worth while to argue. What argue? 250.64(F) is one paragraph. I guess it's not worth it to open the book either.
Thanks for your responses Larry, I like to get the inspector's point of view. I wish more of you guys would participate.
[ October 26, 2004, 04:38 PM: Message edited by: physis ]