Ihave an installation consist of the following

Wood building ,use metal boxesfor recpt. and sw,ent.for raceway. i'm running one hot, one ntrl,and a grnd.
I'm connecting the grnd to recpt. grd screw ,recept. has the spring in the yoke. do I still to have to bond the metel box with a wire
and screw or the recpt. yoke will do the job
{flush mnt}
 
Re: bonding

The "self-grounding" yoke on the device can be used going from a grounded box (250.146(B))to the device not to a box (250.146(A)).