Rick Quarles
How important is bonding a hydromassage motor back to the bus in the panel if the plumbing is all plastic??
Rick Quarles said:How important is bonding a hydromassage motor back to the bus in the panel if the plumbing is all plastic??
Raider would you mind explaining that to some of these inspectors in Texas...
infinity said:This seems top be a common misconception. I have seen guys bonding the motor to the hot and cold water pipes feeding the faucet. This isn't required either.
M. D. said:In this area it had been what the inspector wanted to see, perhaps still does, I have bonded many to the copper water pipe myself. My Question is , is there a downside (or any danger) to bonding the motor to the water pipe?
I can think of a few...M. D. said:Question is , is there a downside (or any danger) to bonding the motor to the water pipe?
2008 680.74 Bonding. All metal piping systems and all grounded metal parts in contact with the circulating water shall be bonded together using a copper bonding jumper, insulated, covered, or bare, not smaller than 8 AWG solid. The bonding jumper shall be connected to the terminal on the circulating pump motor that is intended for this purpose. The bonding jumper shall not be required to be connected to a double insulated circulating pump motor. The 8 AWG or larger solid copper bonding jumper shall be required for equipotential bonding in the area of the hydromasage bathtub and shall not be required to be extended or attached to any remote panelboard, service equipment, or any electrode.