We have a job with an exterior PVC j-box. Coming into the back of the box is nm cable and we are leaving the box with 3/4 Emt. IS there a way to bond this properly.
 
blueheels2 said:
We have a job with an exterior PVC j-box. Coming into the back of the box is nm cable and we are leaving the box with 3/4 Emt. IS there a way to bond this properly.

Bond bushing on the EMT tied to an equipment grounding conductor....or, if the other end of the EMT terminates in a metal enclosure, box....and is bonded to an EGC.
 