according to 250.92 a 2 meter fitting are to be bonded, so we have been requiring contractors to bond meter fitting when they are isolated by pvc, or se cable. 250.142 a allows for the use of the grounded conductor at the supply side of the sevice disconnecting means. which is more appropriate in this application?
 
Meter sockets usually have a screw that bonds the enclosure to the grounded conductor. Likewise for the first disconnect. I'm not sure what your question is:-?
 
As A/A said the meter enclosure is already bonded to the neutral so nothing further is required. Using SE cable or PVC doesn't require any additional bonding of the meter enclosure.
 
Meter sockets usually have a screw that bonds the enclosure to the grounded conductor.
I don't think I've ever seen a modern meter base that sisn't have the neutral terminals either directly bolted to the enclosure, or onto a bracket which was.
 
I agree Larry but the Milbank sockets I use have a bonding screw that could be easily removed thus isolating the meter socket from the grounded conductor. I used the word usually to make that known.
 