The reference was to boosting just one ungrounded leg, to end up with 120V L1-N, 240V L2'-L1, and 149V L2'-N.It would apply if your reference is N'.
Cheers, Wayne
The reference was to boosting just one ungrounded leg, to end up with 120V L1-N, 240V L2'-L1, and 149V L2'-N.It would apply if your reference is N'.
I wouldn't wire a receptacle with that, as the N terminal is expected to be at ground voltage. But for hardwired equipment, where you've carefully checked that it's OK for the N terminal to be at 60V to ground, you could do it.Then use N' instead of N. Perhaps clearly label the outlet, or build it into or onto the load/equipment.
I still like my idea.Sorry, posted in a hurry and forgot to say it is single phase. So now, how to wire the neutral?
The load is a grinder pump for a septic,or sewer system.
Well the pump won't need a neutral, so what does? Is this that septic deal with high water alarm circuit? If so, I fail to see the issue. Deliver legs from xfmr to pump, then just use an untapped leg and neutral for your 120V loads. Am I missing something here? Circuit diagrams sure help.Sorry, posted in a hurry and forgot to say it is single phase. So now, how to wire the neutral?
The load is a grinder pump for a septic,or sewer system.
As I mentioned in my OP, I'm just helping a friend and just by phone. I haven't seen the pump, or diagrams. I'm assuming the neutral is for a control panel.Well the pump won't need a neutral, so what does? Is this that septic deal with high water alarm circuit? If so, I fail to see the issue. Deliver legs from xfmr to pump, then just use an untapped leg and neutral for your 120V loads. Am I missing something here? Circuit diagrams sure help.
The more I think about it no it will be the mentioned ~134. Draw it out to scale- two lines of 120 units intersecting at a 120 degree angle. Now add 16 more units to them and they are both 136 units long. Is 240 between the open ends though.Not the way I'm talking about. I'm saying to wire each secondary to opposite ends of the primary.
Each 104v half gets one half of the boost, maintaining the secondary's center tap centered-ness.
If not connecting the center tap to source neutral, you end up with three ungrounded conductors on your "outputs". Doesn't that go against what it says in 210.9 that was mentioned in post 8?Basically this, but the load neutral would originate at the center tap, but not connect to the source neutral.
View attachment 2578623
I'm lost in the conversation but what in the world does 120* have to do with anything here? Load is single phase. Any single phase, whether in a 1P or 3P service is only a single sine wave. There is no phase offset. but if you split the phase, it would be 180*.The more I think about it no it will be the mentioned ~134. Draw it out to scale- two lines of 120 units intersecting at a 120 degree angle. Now add 16 more units to them and they are both 136 units long. Is 240 between the open ends though.
To get 120 to the common point you need a 180 degree angle and 120 length to each side, just like a true single phase winding.
Your description corresponds to using two separate single coil boost autotransformers to boost L1 relative to N and separately L2 relative to N to get 2 of 3 legs of a 240Y/138V system.The more I think about it no it will be the mentioned ~134. Draw it out to scale- two lines of 120 units intersecting at a 120 degree angle. Now add 16 more units to them and they are both 136 units long. Is 240 between the open ends though.
In post 8, I commented that Exception 1 would apply, as the Exception is not limited to 2-wire circuits.If not connecting the center tap to source neutral, you end up with three ungrounded conductors on your "outputs". Doesn't that go against what it says in 210.9 that was mentioned in post 8?
Exactamundo.I.e. this, but you'd need to check that the load is OK with a neutral that is 60V to ground.
Cheers, Wayne
View attachment 2578626
We're looking at 1ph 208v with two lines and no neutral, it would be 180 degrees, not 120.The more I think about it no it will be the mentioned ~134. Draw it out to scale- two lines of 120 units intersecting at a 120 degree angle. Now add 16 more units to them and they are both 136 units long. Is 240 between the open ends though.
To get 120 to the common point you need a 180 degree angle and 120 length to each side, just like a true single phase winding.
Exception No. 1: An autotransformer shall be permitted without the connection to a grounded conductor where transforming from a nominal 208 volts to a nominal 240-volt supply or similarly from 240 volts to 208 volts.If not connecting the center tap to source neutral, you end up with three ungrounded conductors on your "outputs". Doesn't that go against what it says in 210.9 that was mentioned in post 8?
Sorry, posted in a hurry and forgot to say it is single phase. So now, how to wire the neutral?
my exact thought.
No.We're looking at 1ph 208v with two lines and no neutral, it would be 180 degrees, not 120.
As I mentioned in my OP, I'm just helping a friend and just by phone. I haven't seen the pump, or diagrams. I'm assuming the neutral is for a control panel.