The_G_Man
New member
- Portsmouth, NH USA
I have a case where my conduit run starts in a Class I, Div 2 area, travels underground (regarded as non classified area) and ends back in the same Class I, Div 2 area.
Technically I'm going through two area boundaries (from Div 2 to unclassified back to Div 2) and I would have to put seals within 10 ft of each transition. However, I fail to see how this is a realistic need. I don't mean to reinvent or debate the code but I believe that the intent of having seals is to prevent gas from using a conduit to migrate into an non hazardous area and in my case I just don't see how this can be a concern.
I can't find any undisputable code reference that permits me to NOT install seals at the two boundaries (most of the exceptions listed refer to scenarios that are almost the opposite of mine, such as unbroken metal conduit runs that start and end in non-hazardous location and pass through a Div 2 without any unions, couplings, boxes of fittings)
Does anyone have a code reference I can use to justify not using seals or shall I just bite the bullet and account for them?
Thank you all for your assistance!