B bfmickl Member Location Zebulon, NC USA near Raleigh, NC Jan 6, 2004 #1 When sizing a JB that will contain AC or MC type cables, varying in sizes from #14 to #1 AWG conductors and will also contain splices, wouldn't you have to apply article 314.28(2)?
When sizing a JB that will contain AC or MC type cables, varying in sizes from #14 to #1 AWG conductors and will also contain splices, wouldn't you have to apply article 314.28(2)?
roger Moderator Staff member Location Fl Occupation Retired Electrician Jan 6, 2004 #2 Re: Box Fill AC and MC Cable Yes, specifically the last paragraph of 314(A)(2) Roger