wwhitney
Senior Member
- Location
- Berkeley, CA
- Occupation
- Retired
So with 314.28 applying in lieu of 314.16, then we have, for a box with just one cable entry:Info on #4 conductor from a past thread.
- A Hubbell HBL9450A 14-50 receptacle is 2.44" deep. So 314.24(B)(1) applies, and the box must be at least 2.69" deep internally. That means 314.24(B)(3) is also satisfied.
- If the cable entry to the box is via the back, 314.28(A)(2) Exception applies, and the box only needs to be 1-1/2" deep for compact stranded aluminum #4, or 2" deep for other #4 conductors, to satisfy that. Either way 314.24(B)(1) controls. But the upshot is you could install the receptacle in any 2.75" or deeper double gang (as the Hubbell brand requires a double gang, IIRC), no box volume computation required. If you got a different 14-50 receptacle that is listed for a single gang and 2.5" or less deep, you could put it in a 2.75" deep single gang, assuming you could get it to fit and still comply with the 6" conductor length rule (presumably not going to fit).
- If the cable entry is to the side of the box, then the width is now controlled by 314.28(A)(2), and we need to find the equivalent conduit size for the #4 cable. If we can use any conduit type and conductor insulation we like, you can fit (3) #4s and (1) #8 EGC in a 3/4" conduit, and the required width is 4-1/2". If we stick with reasonable choices like IMC and XHHW-2 insulation, the equivalent conduit size is 1", and the required width is 6". The height is not limited (other than mounting the device).
- If the cable entry is to the top or bottom, then it's same as the side entry case, except now the height has a minimum, and the width is not limited.
How does all that sound?
Cheers, Wayne