I got flagged by the inspector today for excessive box fill , and can't figure out which of us doesn't know how to count.I had a 1900 bracket box stamped at 21.5 cu in. A 1/2" 2 gang ring stamped at 5.5 cu in. was added to that.The box contained 2 hots, 4 neutrals,2 switch legs, and 2 grounds( installation was in 1/2" conduit) all conductors were #14 gauge. Counting the ground once and adding the rest of the wires to the mix, I come up with 18 cu in. Add a double allowance for each device (2) I come up with a grand total of 26 cu in of fill.Have I miscalculated? Would the way I spliced the wires together have anything to do with the fill of the box? One of the hot wires I left about 12" long,skinned two 5/8" loops and spliced to the other hot.Not your typical pigtail, but it according to the inspector each loop I put on a switch counts as two wires fill.To bring this installation into compliance I had to take apart my "loop" splice and add two seperate pigtails for each device.