Therealcrt
Senior Member
- Location
- Kansas City
- Occupation
- Electrician
I will have two sets of 500 KCMill AL with 2/0 AL ground stabiloy MC Cable entering into the back of a junction Box. Out of the bottom of the junction box I’ll have 2 3” EMT conduits piped down about 10 feet into the top of my panel. With the same wire configuration, except THHN. What would be the correct size Junction box I need to make those connections length, width, and depth right now I came up with a 24 x 24 x 6“ junction box