how many runs of 12-2 romex can you have in a regular nail on recp box with a recp in there as well?
8 conductors (Blk and Wht)
1 EGC
2 conductors for device
Total= 11 conductors
Table 314.16(B)
#14= 2 cubic inches/conductor
11 * 2 = 22 cubic inches minimum required
It gets worse. 24.75cubes.