With a well controlled experiment you can not show any benifit by use of capacitor power factor correction for a customer that does not get charged a PF penalty, and the PFC is placed at or within a few feet of the meter.
Following is some data I put in my notes on "Electrical Energy Measurement, Conservation, and Methods to Reduce Your Electric Bill":
1. The motor is an old 1/3 HP 115 V induction motor. Unloaded very poor PF.
2. Test with no external mechanical load.
3. Motor was run long enough to reach thermal stability.
4. Input voltage was held constant at 117.0 V
5. A Kill-A-Watt was the current, VA, and power measuring instrument. This is quite good with varying power factor. A TED ststem is not.
6. Results
Code:
Capacitance Input Input Input Input
mfd Amps Watts VA PF
0 [B]4.71[/B] [B]140[/B] 552 [B]0.25[/B]
30 3.44 141 400 0.34
60 2.30 141 270 0.52
90 1.45 142 168 0.83
102.5 [B]1.33[/B] [B]142[/B] 158 [B]0.90[/B]
120 1.58 143 185 0.78
If the municipal organizations put PFC at the load, switched with the load, and have long wire runs,
then some small saving in energy will occur. But a loaded motor will not have a real bad PF. So there is not a lot of current change. If the motors are single phase capacitor run, then their power factor alone is quite good.
.