Article 725.1 from NEC 2011 states :
"This article covers remote-control, signaling, and powerlimitedcircuits that are not an integral part of a device or appliance."
The handbook has the explanation that it would cover intercom, nurse call,burglary alarm systems and so on.
Then it describes which other sections apply :
725.3 Other Articles
Circuits and equipment shall comply with the articles or sections listed in 725.3(A) through (J). Only those sections of Article 300 referenced in this article shall apply to Class 1,
Class 2, and Class 3 circuits.
(A) Number and Size of Conductors in Raceway. Section 300.17.
However it does not refer to box fill calculations or box sizing explained in 314.28.
Am I missing something on sizing boxes for signal cabling ?