H Hendrix Senior Member Location New England Dec 8, 2008 #1 A local one is selling 2-4/0, 1-2/0, 1#4 alum. for feeders from 200A disconnect to sub panel. This dosen't sound right to me. What say ye?
A local one is selling 2-4/0, 1-2/0, 1#4 alum. for feeders from 200A disconnect to sub panel. This dosen't sound right to me. What say ye?
raider1 Senior Member Staff member Location Logan, Utah Dec 8, 2008 #5 I agree with Ken. 250.122 has a #4 alu. wire good for and equipment grounding conductor for a 200 amp breaker. You are also permitted to size the neutral to the maximum unbalanced load. See 220.61. Chris
I agree with Ken. 250.122 has a #4 alu. wire good for and equipment grounding conductor for a 200 amp breaker. You are also permitted to size the neutral to the maximum unbalanced load. See 220.61. Chris
H Hendrix Senior Member Location New England Dec 8, 2008 #6 Thanks guys, I'm on the right page now.:grin