A local one is selling 2-4/0, 1-2/0, 1#4 alum. for feeders from 200A disconnect to sub panel. This dosen't sound right to me. What say ye?:confused:
 
I agree with Ken.

250.122 has a #4 alu. wire good for and equipment grounding conductor for a 200 amp breaker.

You are also permitted to size the neutral to the maximum unbalanced load. See 220.61.

Chris
 