ceb58
Senior Member
- Location
- Raeford, NC
I got a call around 5:00pm from a regular customer. The HO is having his bath remodeled that was added on in 1986. The carpenter tried to "short" the circ. for the lights to remove a stud, the breaker would not trip. HO replaced breaker with new one still will not trip breaker. Here is what I found ITE panel installed in 1981, the breakers that feed the bath were all tandem "piggyback" breakers. I tried shorting out the ungrounded cond. with EGC lights would dim but not trip breaker 15 amp. I then tried the grounded conductor same thing lights would dim breaker would hold. I did some more looking and found that some where the ungrounded cond. from the 15 amp is tied to a ungrounded cond. feed from a 20 amp tandem "they luckily landed on the same phase" I disconnected the wire from the 20 amp breaker and caped it off, I then went back and tried to trip the breaker same thing it will not trip. I think I know what has happened to a point. The 15 amp circ. feeds some lighting in the older part of home. I think that some one pulled a new 20 amp circ. for the recpt. and landed in a j box with the 15 amp. circ. and tied them together. But what I cannot understand is WHY cannot trip this breaker :-? . Going in the morning to find the j box in attic.