So 550.32 A is for MOBILE homes
I am working on Manufated home So 550.32 B is what I work off of. It states no Distance for Service disconect
So then 230.70 a 1 says either OUT side or nearest point of entry
230.85 needs a Emergency Disconnect outside
Asking because I have a New Meter main about 50' in from of Manufactured home, I was origanly planning to just come off that and feed the old panel inside.
Seems I am good. Can't find a distance requirement for the Service disconnect
Service Disconnect all is Emergency Disconnect. And it does not need to be within 30' cause its not a Mobile home. its on permeant foundation.
Oregon has no Revisions under 550.
Reassurance is all I need
I am working on Manufated home So 550.32 B is what I work off of. It states no Distance for Service disconect
So then 230.70 a 1 says either OUT side or nearest point of entry
230.85 needs a Emergency Disconnect outside
Asking because I have a New Meter main about 50' in from of Manufactured home, I was origanly planning to just come off that and feed the old panel inside.
Seems I am good. Can't find a distance requirement for the Service disconnect
Service Disconnect all is Emergency Disconnect. And it does not need to be within 30' cause its not a Mobile home. its on permeant foundation.
Oregon has no Revisions under 550.
Reassurance is all I need