Branch circuit conductors/Home Runs

Status
Not open for further replies.

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
I believe a branch circuit conductor is from the last OCPD to the load/device/equipment. So if you had a home run pipe coming out of a panel with 6 cicruits to a home run box would that be considered branch circuit conductors? Thanks.

If you had a pipe from a panel to a disconnect for a motor would that be a branch circuit? Or would it bee from the disconnect to the motor? Thanks.
 
Last edited:

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
If there are no other OCPD then each cir that was run is a branch circuit. The splices do not matter so the entire run is the branch circuit. The homerun is generally considered the wire from the breaker to the first device or JB.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
The NEC defines the term branch circuit:

Branch Circuit. The circuit conductors between the final
overcurrent device protecting the circuit and the outlet(s)
 