F frisbkm Member Jul 2, 2003 #1 What is the minimum size branch circuit conductor required for a 10 hp,3-phase,230 volt induction motor using 60 degree C insulation?
What is the minimum size branch circuit conductor required for a 10 hp,3-phase,230 volt induction motor using 60 degree C insulation?
charlie Senior Member Location Indianapolis Jul 2, 2003 #2 Re: Branch circuit conductors This sounds like a homework question.
B bphgravity Senior Member Location Florida Jul 2, 2003 #3 Re: Branch circuit conductors 1. Find the F.L.C. of the motor per Table 430.150. 2. Find the branch-circuit conductor requirements per 430.22(A). 3. Use Table 310.16 to find conductor size. Use Table 250.122 to find EGC size.
Re: Branch circuit conductors 1. Find the F.L.C. of the motor per Table 430.150. 2. Find the branch-circuit conductor requirements per 430.22(A). 3. Use Table 310.16 to find conductor size. Use Table 250.122 to find EGC size.
P pierre Senior Member Location Westchester County, New York Jul 2, 2003 #4 Re: Branch circuit conductors Hello Bryan I like your answer, give him the method and let him figure the answer, you must be a teacher. Good job! Pierre
Re: Branch circuit conductors Hello Bryan I like your answer, give him the method and let him figure the answer, you must be a teacher. Good job! Pierre