big john
- Portland, ME
I recently encountered a 12 pole subpanel on 30A breaker: Eleven 15A circuits, one 20A circuit. Supplied almost all the lighting and convenience receptacle loads for two floors of a large house, including some heavy-duty intermittents: disposal, compactor, etc. They'd never had a problem with overloading.
Had I been the installer, a lot of ampacity in that sub would've probably gone to waste: Lighting circuits all calculated to 80%. Seven or eight receptacles on one 20A breaker.
The problem is I take a lot of pride in my work, and because of that, I never want the homeowner to be inconvenienced by my design: They go to plug the vacuum cleaner into a branch circuit that already has the entertainment center on it and it ends up tripping the breaker.
To avoid that, I end up trying to plan for any eventuality and probably wasting a lot of available circuit space because of it.
The ultimate question being: How do you guys generally figure residential branch circuit loads? Any rules-of-thumb or general load values for receptacles/lighting or anything I can use in the future that might help me learn to better distribute available power?
Thanks a million.
-John
Thanks a million.
-John