ryan_618 said:The Article 220 references are not for branch circuits. The branch circuit requirements are found in:
410.101 (B) Connected Load. The connected load on lighting track shall not exceed the rating of the track. Lighting track shall be supplied by a branch circuit having a rating not more than that of the track.
I would say that 220.14(D) covers it. With that said, how do you determine what the maximum wattage of lamps for the track light?RB1 said:Ryan,
Section 220.10 requires that branch circuit loads be calculated as shown in 220.12, 220.14, and 220.16. There is no reference to Article 410. Considering that track lights are not specifically listed in "other loads" found in 220.14, wouldn't 220.14(L) apply?