I respectfully disagree. Some of us feel that the feeder and branch definitions are written in a way that allows some circuits/wires to be both at the same time.
A classic example of this would be a single circuit that feeds a load directly (creating an outlet) and also continues on to feed a fused disconnect or even a panelboard.
Since some of the wires connect a load directly to the upstream disconnect, those are branch wires. Since the same or other wires in the circuit connect one OCPD to another OCPD they are also feeder wires.
Some say that since such a circuit would be both a branch and a feeder it must not be legal in the first place. I say both branch rules and feeder rules apply to the same circuit, and it may not be a great design even if legal.