Micksbroke
- Gainesville, Fl.
I have had a new type of water heater to hook up. Its from Germany. Its a instant hot type.
The book says it requires 2- 40a circuits. 1 per canister, But the Name plate says 52a combined (both canisters) So I ran 2-#6 and grd. on a 60a breaker. So I Took the Polaris taps and split circuit at the unit, to both canisters. (208v each)
I thought the Tap rule applied and made since. He says it does not apply. I treated it like a wall oven with a cook top on same circuit. He said that's not legal also. (Am I reading 210.19 (A) 3 wrong?)
Did a load check by running hot water for 10min +/-. Its 52a on the money. It's not considered a continuous load.
The inspector says he don't like it... Does 210.19 (A) 4 not apply?
The WH book states 2 circuits. But that's 2- 2pole circuits per 1 unit. No UL listed handle tie available for two 2pole breakers. This could be a dangerous situation and the Tap was less dangerous...I thought.
Any suggestions or guidance is valued.