I guess I was thinking in terms of air restriction, not sure I'm correct now.more load on the motor...
I was going off my furnace motor, which monitors amperage and will increase speed as the filter gets dirty to self correct for proper air flow.
You thinking wrong in both cases. Plugged furnace filter does restrict air flow, your furnace may compensate by increasing motor speed but will still take same amount of work to move same amount of air. . Actual load on motor is determined by amount of air the blower is moving. More CFM = more load.
If you restrict airflow and maintain same motor speed you will have less load. On the typical household hair dryer you will not restrict flow very much before high limit shuts the unit off. I've had to clean wifes hair dryer a few times for this very reason. Resistance of element remains constant no matter how much air is flowing.