Branch circuits to shed?
dbill27
ALASKA
I have a pole mounted meter/panel combo about 30 feet away from a small utility shed that exists just to house a well pump and pressure tank inside. I need power to to this shed only for the pump motor inside and also would like to bring a branch circuit over for a receptacle and small light for inside. Does this small building need it's own sub panel or can I simply bring 2 circuits over from my panel on the utility pole? Do these branch circuits need a disconnect on or at the building even thought the breaker is within view?
Was planning on bringing circuits underground in pvc to the inside of the shed and hitting a junction box. There is another building that will be built in the future that will need it's own sub panel that will also be fed from this meter/panel combo on utility pole, not sure if that's relevant in any way.
I mostly do industrial work so this is a little out of my area of expertise but I'm helping a friend out with their project. Any help is appreciated.
A remote building can only have one branch circuit, or feeder to it. You would need to run a 4-wire over and put in a subpanel.
Now they do allow a MWBC to count as a single circuit. So if your pump was say a 20A 120v pump, you could run a MWBC and put the pump on one leg and the other circuit on the other. You would need a disconnect, and that could be a simple 2-pole toggle switch.
pull 4 wires at the least, even if you don't subpanel in there later.
you're already laying the pvc, work, time. in todays costs, what's a $40 subpanel and $30 in breakers?
i did the exact same idea. mbwc for a 120v light/plug and pump. well, i wasted my time when i went to a 240v pump. A no-no bandaid is to use the ground as a neutral, but i did that only long enough until i went through the work of pulling a 4th wire.
never think of the project in front of you, always think of the next one you don't want to do!
Thanks.
Good Advice thank you.
I'm going to assume that if I put a small sub panel in this building, a main breaker on that panel meets the requirements of the disconnect? On a related thought before I look thru the code book, is there anything not allowing the back feeding of a breaker to serve as the main breaker and disconnect of a small sub panel?
Yes, a main breaker would count as the disconnect. It does have to be located nearest the point of entry of the conductors.
You can backfeed a breaker but you would have to use a breaker hold down kit.