Copperclad
Member
- Location
- Merritt Island, FL USA
Howdy Fellas!
I had a question regarding an insta hot type water heater. According to the cut sheet it is rated 3500w@120 volts and requires a min, ckt ampacity of 30 amps. Seems pretty cut and dry to me, so off to the van I go for a fresh roll of 10/2 MC (this a commercial build out by the way) A co-worker starts flappin' his chops about needing 8 wire on a 40 amp breaker.... I thought a branch ckt. could be loaded to 100% capacity if its not considered a continuous load. Am I mistaken, or missing something here?
Many Thanks,
Ted
I had a question regarding an insta hot type water heater. According to the cut sheet it is rated 3500w@120 volts and requires a min, ckt ampacity of 30 amps. Seems pretty cut and dry to me, so off to the van I go for a fresh roll of 10/2 MC (this a commercial build out by the way) A co-worker starts flappin' his chops about needing 8 wire on a 40 amp breaker.... I thought a branch ckt. could be loaded to 100% capacity if its not considered a continuous load. Am I mistaken, or missing something here?
Many Thanks,
Ted