I am a student in code classes. Regarding 210.19(A)1 [2002 NEC] and the exception. The instructor gave a complex explanation that I did not get.
From (1): Branch-circuit conductors shall have an ampacity not less than the max. load to be served. Where a branch circuit supplies continuous loads or any combination of continuous and non-continuous loads, the min. branch circuit conductor size , before the application of any adjustment or correction factors, shall have an allowable ampacity not less than the noncontinuous load plus 125 percent of the continuous load.
So, if I have a non-continuous load of say 10 amps and an appliance for a continuous load of 18 amps, then I would take 10 amps plus (18 amp x125%) for a total of 32.5 amps... is this part correct or not?
Then the exception: Where the assembly, including the overcurrent devices protecting the branch ckts, is listed for operation at 100% of its rating, the allowable ampacity of the branch circuit conductors shall be permitted to be not less than the sum of the continuous load plus the noncontinuous load.
Now what's the difference??? Please give a few examples.
Bob
From (1): Branch-circuit conductors shall have an ampacity not less than the max. load to be served. Where a branch circuit supplies continuous loads or any combination of continuous and non-continuous loads, the min. branch circuit conductor size , before the application of any adjustment or correction factors, shall have an allowable ampacity not less than the noncontinuous load plus 125 percent of the continuous load.
So, if I have a non-continuous load of say 10 amps and an appliance for a continuous load of 18 amps, then I would take 10 amps plus (18 amp x125%) for a total of 32.5 amps... is this part correct or not?
Then the exception: Where the assembly, including the overcurrent devices protecting the branch ckts, is listed for operation at 100% of its rating, the allowable ampacity of the branch circuit conductors shall be permitted to be not less than the sum of the continuous load plus the noncontinuous load.