200124-1649 EST
I my previous post I failed to mention that I did not perceive flicker in the incandescent bulb in the voltage change measurement at the main panel ftrom the 12 A heater load.
Suppose the voltage changes at the main panel were much greater than I measured. For example --- suppose a 2.2 V drop in voltage across the heater was observed when the heater was turned on, and with a voltage change increase of 1.4 V for the unloaded side. Now the ratio is 1.57 instead of 2.
Also it would be useful to be looking at the hot line to hot line voltage change between no heater and heater.
At this time we have insufficient information to judge whether there is a high resistancer neutral and/or or hot wire power company problem.
If there are no major voltage changes at the input to the main panel, the above tests will tell us, then the high trsistancre is in the panel or after.
.