20 amps into the dirt, maybe if it is a massive electrode, such as a CEE if it is a ground rod something tells me the dirt around the rod dries up some and current begins to decrease.
OP said there was same problem with old water heater and it was replaced. If drawing 20 amps that is 2400W @ 120 or 4800W @ 240, unless it is a million gallon tank it probably eventually either reaches a setpoint, kicks out the high limit, or starts to bleed pressure from the relief valve if there isn't heated water leaving the tank.
If it is a fault in wiring you should have a pretty good hot spot somewhere that should burn itself out or start a fire or both.
I think there is a water leak downstream from the heater.
All of a sudden an old water heater started drawing a non stop 20 amps. Brand new water heater was installed by the plumber. We let it fill all the way up before we energized the circuit. Circuit still draws a non stop 20 amps.