Those are indeed Zinsco. Here in So Cali we have a ton of those panels.
Breakers are so-so, bus connections are fair to very poor, and replacement breakers are very expensive. Most Zinsco panels have serious wire-bending space issues.
I have seen many bus failures and a few cases of "FPE syndrome" where the breaker would not trip under an overload or fault.
See
THIS VIDEO for a graphic demonstration.
Yea I like that video, back fed widow maker generator back feeding a zinco panel:roll:
that is the same panel as in the OP.
They got the name "No Blow Zinsco" for a reason
you have a 2-pole 50 for a range
2-pole 30 for AC
2-pole 20 for oven
1 double 1/2 space 20
1 double 1/2 space 15
1 full space 15
1 full space 20
One remarkable aspect about Zinsco was the ability to change which leg the breaker is on by just relocating the buss clip on the back, you could even do this to have a double pole be on the same phase, why would you, I do not know, but with MWBC's it made it great with the half space ones.
But at the same time was one of the major failure of the installers not looking to see were the clip was when using MWBC's
Oh and don't ever install clips in both slots or it will go boom when pluged in.
The only other one I knew that had this option was the old Square D round buss panels.