I received a call for a home without power. I have something odd taking place and don't know of any solutions here and need some suggestions on this one. I will give you facts then some pictures.

Information:
125A Breaker using 3/0 Aluminum when 2/0 is the requirement. Aluminum has 0 give as they left no extra wiring at all and they gave the wire a hair cut to fit into the breaker causing it to arc in the terminals of the breaker. It melted some of the undersides of it. For testing, I replaced the breaker as I wasn't getting voltage from the terminal to ground indicating bad breaker. After testing I noticed 0 volts when testing across L1 and L2. Here are the photos and tell me what you think.
52381168103__6327EE5B-50D1-4FC4-A783-48BF1AF3F0D8.jpg52381165723__A4E8F941-9DC9-44E3-8E2E-DCA6BD500AAF.jpg52381172654__D89D6640-C434-489A-90DC-69601007EAA3.jpg52381174747__A174B6CF-D93E-4256-9001-6F3EB943A0BB.jpg52381209981__299BAC4B-1FD3-4251-893D-C943DDF9EDB7.jpg52381278280__5929E556-2334-4D30-AA56-A916F850DE69.jpg52381277550__56733141-5C15-4DBF-AC0E-82E0C3A37B62.jpgIMG_0905.jpg
 
I received a call for a home without power. I have something odd taking place and don't know of any solutions here and need some suggestions on this one. I will give you facts then some pictures.

Information:
125A Breaker using 3/0 Aluminum when 2/0 is the requirement. Aluminum has 0 give as they left no extra wiring at all and they gave the wire a hair cut to fit into the breaker causing it to arc in the terminals of the breaker. It melted some of the undersides of it. For testing, I replaced the breaker as I wasn't getting voltage from the terminal to ground indicating bad breaker. After testing I noticed 0 volts when testing across L1 and L2. Here are the photos and tell me what you think.
View attachment 18170View attachment 18171View attachment 18172View attachment 18173View attachment 18174View attachment 18175View attachment 18177View attachment 18176
Looks like a power company problem bad transformer.?

Sent from my SM-T350 using Tapatalk
 
It's definitely on their side. When you open the breaker you remove almost all resistance. That is why you at least get 120v . When you close the breaker your resistance goes up voltage goes down . And may have lost 1 phase.

Sent from my SM-T350 using Tapatalk
 
I would recommend redo on that service! Looks hazardous! Where is the ground electrode conductor. And is the neutral and ground separate at breaker panel. Only looks like 3 wires going out of back to somewhere.

Sent from my SM-T350 using Tapatalk
 
Isn't this the same question you asked the day before here? http://forums.mikeholt.com/showthread.php?t=185939

-Hal

Son of a gun!! I thought I didn't hit the submit button because I was writing it but didn't think I hit the sent button and I got on a phone call. Since I didn't hit the notifications check box I had no idea people were responding to it, I now see a bunch of responses. I'm going to that thread now, thank you.
 