Breaker Doesn't Trip?

Status
Not open for further replies.

anbm

Senior Member
We have 400A thermal magnetic breaker to feed a 600A MLO panel, this panel feed (4) elevators at 70FLA (didn't know inrush current). We meter the panel and at certain time, the meter reads 850A at phase A and other time, it reads 1,200A at phase B. The 400A breaker never tripped. I am wondering why. Thanks!
 

zog

Senior Member
Location
Charlotte, NC
We have 400A thermal magnetic breaker to feed a 600A MLO panel, this panel feed (4) elevators at 70FLA (didn't know inrush current). We meter the panel and at certain time, the meter reads 850A at phase A and other time, it reads 1,200A at phase B. The 400A breaker never tripped. I am wondering why. Thanks!

How long are those currents present?

What is the breaker type (CAT#)?
 

iwire

Moderator
Staff member
Location
Massachusetts
Along with the great answers you have gotten I would ask how sure are you of your meter and it's settings? Is the meter set correctly for, or even compatible with the probe you are using?

Can you try it against a know load?

Can you look up the trip curves for the breaker you have?
 

kingpb

Senior Member
Location
SE USA as far as you can go
Occupation
Engineer, Registered
According to the trip curve for a 400A Eaton-CH HKD breaker with fixed thermal trip, and adjustable magnetic trip, the lowest setting on the adjustable portion is 5x (5 x 400 = 2000A). The trip curve indicates that the 1200A would need to be present from between 60 secs-140 secs (error band)before the breaker would trip.

Your measurements were most likely catching the inrush from the motors due to elevator operation, and it was not the continuous amount of current.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
If you had two elevators start at the same time, you would see probably around 840A (70 x 6 x 2); 3 at the same time would read 1260A. Do those values look familiar? :)
 

mxslick

Senior Member
Location
SE Idaho
If you had two elevators start at the same time, you would see probably around 840A (70 x 6 x 2); 3 at the same time would read 1260A. Do those values look familiar? :)

Excellent deduction Dr. Evil. :grin:

I agree, looks like OP captured the inrush of one or more elevators starting.
 

steve66

Senior Member
Location
Illinois
Occupation
Engineer
Did anyone there key-up a two-way radio while you were taking the measurments?

I've seen that cause a current reading to show 1000-2000 amps while the load was really only a couple of hundred amps.

Steve
 