"I have the control wires running from the pit in 2" pvc to the 10x10 pvc box & then I'll finish it from there".
"Question, in regards to the 2" pvc coming from the pit/fiberglass tub where the control wires come from do I need to foam the pvc in case of back flow up into the main box. I know the float switch will turn it off etc. but I was just wondering. My answer is no but I need a confirmation."
If that conduit is continuous from the tank to the control, you may need to install a seal fitting in the pipe to prevent any sewer gas (methane) from backing up thru the conduit and into the control housing.
It can cause a hazard if enough gas accumulates in the disconnect/controls. One spark and look out.
I was required to install these fittings on a couple of commercial systems that I installed where the conduit was continuous between the tank and control box/disconnect.
The ones that I used looked like a plumbing "wye" strainer. After the wire was pulled, the plug in the fitting was removed and a sealing compound was poured in to seal around the wires and plug the passage.
On the smaller systems, I used a 5 conductor direct burial cable. That way I didn't have to run the conduit all the way to the tank, only far enough to protect the cable as it emerged from the ground to the disconnect. This way I didn't need to "block" the pipe.
Just a thought
steve